Overview: Sub-categories and References
Building Science and Systems falls under a single sub-category in Examitect's ExAC study plan. Two primary references (CHING and CHOP) plus seven supplementary guides are listed, which signals that ExAC questions test breadth across all construction systems rather than depth in one area.
| Reference | Chapters / Sections | Primary focus for this topic |
| CHING | Chapters 3-8 | Visual assembly logic for foundation, floor, wall, and roof systems, moisture and thermal protection, and doors and windows |
| CHOP | Chapters 2.5, 5.5 | Canadian practice context and architectural coordination of building systems |
| Building Envelope Thermal Bridging Guide | Sections 3, 4 | Linear transmittance (psi values), effective R-values, and continuous insulation strategies |
| Canadian Wood-Frame House Construction | Chapters 5, 6-8, 9-11, 12-16 | Framing details and envelope assembly for Canadian residential construction |
| Heating, Cooling, Lighting | Chapters 2, 3-4, 15 | Passive design, solar geometry, thermal mass, and climate-responsive strategies |
| Why Houses Need Mechanical Ventilation Systems | All | 0.3 ACH minimum, HRV/ERV selection, exhaust-only risks, combustion safety |
| Designing Exterior Walls: Rainscreen Principle | All | Pressure equalization, drained and ventilated cavities, face-sealed vs rainscreen comparison |
| Windows: Overview of Issues | All | U-value, SHGC, visible transmittance, frame thermal performance, condensation risk |
| Performance of Thermal Insulation: Basement Walls | All | Below-grade thermal performance and exterior vs interior insulation placement |
What Building Science and Systems Is
Building science is the study of how physical forces move through a building: heat travels from warm to cold, water moves from high to low pressure, air flows from high to low pressure, and loads travel from point of application to support. Every prescriptive requirement in a building code is a simplified answer to one of those physical questions.
The ExAC tests this topic at a practical level. Given a building situation, you should be able to identify which system is the problem, why it is failing, and what the correct intervention is. You will not be asked to perform engineering calculations, but you will be expected to know the right order of magnitude for key numbers, the correct principles for each system, and the right order of operations when addressing a multi-layer problem.
Building Science and Systems connects directly to other Section 3 topics. Assemblies and Detailing asks you to draw the correct layers; Materials and Construction Fundamentals asks you to choose the right material. This topic is where you understand why each layer exists and in what order it belongs.
Exam tip
When a question describes a building problem, first identify which of the four control layers is failing. Then choose the answer that fixes that layer, not the answer that treats the symptom from a different system.
8.2 Understand construction principles and systems
This is the verbatim text of the single sub-category in Examitect's ExAC study plan for this topic. It is deliberately broad: "construction principles and systems" spans every physical system in a building from the footing to the roof membrane to the ventilation unit.
"Construction principles" refers to how individual assemblies behave: why a footing must be below frost depth, why a vapour retarder belongs on the warm side, why wood shrinks across the grain and not along it. These are physical and material principles, not code-specific rules.
"Systems" refers to how elements interact: the structural system carries loads; the building envelope separates interior from exterior conditions; the mechanical system maintains interior air quality and temperature. An ExAC question on this sub-category may ask about a single system in isolation, or may describe an interaction between systems, such as a condensation problem caused by a thermal bridge in the structural system.
How questions are structured
Expect both definition-style questions ("what is a thermal bridge?") and scenario-based questions ("a wall assembly is showing condensation inside the insulation layer; which control layer is misplaced?"). Questions draw from CHING chapters 3 through 8, CHOP chapters 2.5 and 5.5, and the seven supplementary references listed in the study plan.
Foundations
A foundation transfers building loads to the soil and protects the structure from frost heave, settlement, and moisture. CHING chapter 3 covers foundation systems; Canadian Wood-Frame House Construction chapters 5 and 6-8 address below-grade details in Canadian residential contexts.
Soil and bearing
Soil bearing capacity is typically 100 to 200 kPa for competent soils and much higher for rock. Clay soils are prone to settlement under sustained load and frost heave when saturated and frozen. Granular soils (sand, gravel) drain freely and have predictable bearing. Organic soils (peat) are unsuitable for direct foundation bearing and require deep foundations or soil improvement.
Frost depth and frost heave
In Canada, frost depth ranges from about 1200 mm in milder southern regions to 2400 mm or more in northern areas. Frost heave occurs when saturated soil freezes and expands upward; the force can lift and crack shallow footings. All footings must bear below the local frost depth, or the foundation must be designed to resist heave forces (helical piles or grade beams in poor soils).
Foundation types
- Slab-on-grade: concrete slab on a prepared granular base; economical; requires perimeter or under-slab insulation in cold climates to prevent frost penetration beneath the slab.
- Crawlspace: shallow foundation with accessible underfloor space; a vapour barrier on exposed soil is essential; the perimeter wall is a significant thermal bridge if uninsulated.
- Full basement: most common in cold-climate Canada; greatest frost depth protection; habitable when properly insulated and waterproofed.
- Deep foundations: driven steel, concrete, or timber piles; helical piles; caissons; used where surface soils cannot support building loads or in permafrost areas.
Below-grade moisture control
Dampproofing (bituminous coating) controls vapour diffusion and minor moisture. Waterproofing (sheet membrane or liquid-applied) handles hydrostatic pressure where groundwater may accumulate. A drainage layer (granular backfill or dimple-mat drainage board) and a perforated perimeter drain carry groundwater away before it reaches the wall. Exterior basement insulation, per the supplementary reference on basement wall thermal performance, keeps the wall surface above the dew point and reduces the risk of condensation on the interior face.
Wood Light Frame Construction
Wood light frame is the dominant residential and small commercial construction method in Canada. CHING chapters 4 through 6 (floor, wall, and roof systems) provide the visual vocabulary; Canadian Wood-Frame House Construction chapters 6 through 16 cover Canadian-specific framing, envelope, and finishing details.
Platform frame vs balloon frame
Platform framing (current standard): each storey is built as a complete platform. Floor framing is erected, a subfloor deck is applied, and wall studs one storey tall bear on that deck. Each level is self-supporting before the next begins, which simplifies construction sequencing. The cumulative disadvantage is wood shrinkage: each floor assembly (rim joists, plates) loses 3 to 5 mm of height as green lumber dries, which accumulates over multiple storeys and affects cladding attachments and plumbing penetrations.
Balloon framing (historical): studs run continuously from the sill plate to the roof plate, two or more storeys without interruption. This eliminates differential floor-to-floor shrinkage but requires fire blocking installed horizontally between studs at each floor level (tall stud cavities create a chimney effect). Balloon framing is rarely used in new construction.
Key components
- Sill plate: pressure-treated lumber anchored to the foundation; transitions from masonry or concrete to the wood frame. Requires a sill gasket for air sealing.
- Rim joist (band joist): closes the floor assembly at the perimeter; a significant thermal bridge and air leakage location if not insulated and air-sealed.
- Stud: typically 38x89 mm (nominal 2x4) at 400 mm on centre for most residential walls, or 38x140 mm (2x6) where additional insulation depth is needed.
- Double top plate: two horizontal members at the top of the wall; laps at corners and intersections to transfer loads and tie the frame together.
- Header: the beam spanning a door or window opening; transfers loads to the jack studs on each side. Header depth depends on span and load.
- Jack stud (trimmer stud): the shorter stud that directly supports the header; the full-height king stud runs beside it.
Shrinkage
Wood shrinks and swells perpendicular to the grain (across the width and thickness of a board), not parallel to the grain. In platform framing, every horizontal piece of wood in the floor assembly is oriented with grain running horizontally, so dimensional change accumulates vertically. This affects differential movement between the wood frame and any non-shrinking element (concrete, masonry, steel) and must be accounted for when detailing cladding attachments and structural connections to other materials.
Structural Systems
CHING chapters 4 through 6 cover floor, wall, and roof systems across the common structural materials. Structural questions on the ExAC test principles rather than calculations: how loads travel, what resists lateral forces, and the basic vocabulary of each system.
Load types and typical values
| Load type | Definition | Typical values |
| Dead (D) | Permanent weight of the building | Floor assembly: 1.5-2.5 kPa; Roof assembly: 0.5-1.5 kPa |
| Live (L) | Occupancy loads: people, furniture, movable equipment | Residential floors: 1.9 kPa; Office: 2.4 kPa; Assembly: 4.8 kPa; Stairs: 4.8 kPa |
| Snow (S) | Ground snow accumulation, modified for roof exposure and slope | 1.0 to 3.0 kPa across Canada; higher in mountain regions |
| Wind (W) | Lateral and uplift pressure from wind | Varies by location, exposure category, and building height |
| Seismic (E) | Lateral force from ground acceleration | Varies by zone; most significant in coastal BC and the St. Lawrence-Ottawa valleys |
Load path
Gravity loads travel from point of application downward to the nearest support and ultimately to the foundation: roof loads transfer to rafters or trusses, to bearing walls or beams, to columns or bearing walls, to footings, to soil. Tributary area is the floor or roof area that delivers load to a single member; doubling the tributary area doubles the load on that member.
Lateral resistance
Wind and seismic forces are horizontal and require a dedicated lateral resistance system:
- Shear walls: walls sheathed and connected to act as vertical plates resisting in-plane lateral forces. In wood frame, structural sheathing (plywood or OSB) nailed at close spacing provides shear resistance. Shear walls must be tied to the foundation to resist overturning.
- Diaphragms: floor and roof systems that act as horizontal plates, collecting lateral loads and transferring them to shear walls. A floor diaphragm can transfer wind load from cladding on upper walls to the shear walls below.
- Collectors (drag struts): horizontal members that transfer diaphragm forces into shear walls where the shear wall does not extend the full length of the diaphragm.
Steel and mass timber
Wide-flange sections (W-shapes) are the standard beam and column for structural steel frames. HSS (hollow structural sections) serve as columns and exposed architectural members. Open web steel joists (OWSJs) provide economical long-span floor and roof framing; the open web allows mechanical services to pass through without cutting structural members. Mass timber has grown in use for low- to mid-rise construction: CLT panels serve as floor, wall, and roof elements; glulam serves as beams and columns. Both offer predictable structural performance and reduced embodied carbon relative to steel and concrete.
Building Envelope: The Four Control Layers
The building envelope separates the conditioned interior from the exterior. It must control four things: water, air, vapour, and heat. Each has a dedicated control layer, and each layer must be continuous across the entire envelope, including at junctions, penetrations, and transitions between assemblies. CHING chapter 7 covers moisture and thermal protection; the Building Envelope Thermal Bridging Guide sections 3 and 4 provide quantitative data on thermal performance.
1. Water control
The primary line is the cladding (brick, stucco, siding), which sheds the majority of rainwater. The secondary line is the drainage plane: a water-resistive barrier (WRB) or self-adhered membrane that catches water penetrating the cladding and directs it outward. Flashings are the tertiary line at every junction where the drainage plane is interrupted: at sills, heads, rough openings, and where walls meet roofs, foundations, or other materials.
The rainscreen principle adds a drained and ventilated cavity between the cladding and the WRB. When the air pressure behind and in front of the cladding is equalized, there is no driving force to push water through joints. Any water entering the cavity drains at the base. Rainscreen cladding is the standard in high-precipitation Canadian climates.
2. Air control
Air leakage accounts for far more moisture movement through a wall than vapour diffusion. The air barrier must be continuous and connected at every joint. It can be at the interior surface (polyethylene sheeting doubled as air barrier), at the sheathing (taped OSB), or at the exterior (rigid board with taped seams). Regardless of position, all penetrations (pipes, wires, ducts) must be sealed at the air barrier plane.
3. Vapour control
In cold climates, water vapour diffuses from the warm, humid interior toward the cold exterior. If it reaches a surface below the dew point, it condenses. In cold climates (most of Canada), the vapour retarder belongs on the warm (interior) side of the insulation. Class I vapour retarders (polyethylene) are under 0.1 perms; Class II (kraft paper) are 0.1 to 1.0 perms; Class III (latex paint) are 1.0 to 10 perms. Smart vapour retarders change permeability with humidity, blocking diffusion in winter while allowing drying in summer.
4. Thermal control
Insulation resists heat flow (R-value = 1/U-value). The effective R-value of an assembly is lower than the nominal R-value of the insulation alone because of thermal bridges: paths of higher conductivity that bypass the insulation layer. Wood studs reduce effective wall R-values slightly; steel studs can reduce effective R-values by 30 to 50 percent compared to the cavity insulation rating because of the high conductivity of steel.
Continuous insulation placed outboard of the structural frame, without interruption by framing members, eliminates stud bridging. The Building Envelope Thermal Bridging Guide (sections 3 and 4) expresses bridge magnitude as linear transmittance (psi, W/m K) per metre of bridge length or point transmittance (chi, W/K) per bridge. Common catalogued bridges include shelf angles supporting brick cladding, balcony slab extensions through the envelope, window frame connections, and cladding-support brackets. Exterior continuous insulation over these bridges is the most effective strategy.
Key rule
In a wall assembly from exterior to interior: water barrier (cladding), drainage plane, structural sheathing, framing, insulation, vapour retarder, interior finish. The air barrier can be at any layer as long as it is continuous. The vapour retarder must be on the warm side (interior) in cold climates.
Roofing Systems
CHING chapter 6 covers roof systems, with moisture and thermal protection following in chapter 7. Roofing questions typically ask you to match the system to the slope, identify drainage requirements, or diagnose ice dam formation.
Low-slope roofing (slope below 1:6)
Low-slope systems rely on a continuous waterproofing membrane rather than the overlapping-shingle principle. Common systems:
- Built-up roofing (BUR): multiple plies of felt embedded in bitumen, topped with gravel. Long service life; heavy (requires structural consideration).
- Modified bitumen: SBS- or APP-modified asphalt in a 2-ply system; applied by torch, hot asphalt, cold adhesive, or self-adhered.
- Single-ply membranes: EPDM (rubber), TPO (thermoplastic polyolefin), or PVC; adhered, mechanically fastened, or ballasted; lighter than BUR.
- Inverted (PMR/IRMA) assembly: membrane placed on the structural deck first, then insulation above the membrane. The insulation protects the membrane from UV and temperature cycling, extending membrane life. Water must be filtered before it reaches the membrane drain.
- Green roofs: extensive (growing medium under 150 mm, sedums and grasses, lower structural load) vs intensive (growing medium over 150 mm, deeper planting and trees, higher structural and waterproofing requirements).
Positive drainage is required on all low-slope roofs: minimum slope of 1:50 (20 mm/m). Primary drains must be supplemented by overflow scuppers or secondary drains to handle blockage; overflow drainage is sized to handle the design rain event without exceeding the structural capacity of the roof.
Steep-slope roofing (1:6 or steeper)
Steep-slope systems shed water by gravity using overlapping elements. Asphalt shingles require a minimum slope of about 1:3, or 1:6 with a self-adhered underlayment. Metal roofing (standing seam, corrugated) can work at lower slopes with appropriate underlayment. All steep-slope systems require an underlayment between the sheathing and finish material, and a self-adhered ice-and-water shield at the eaves.
Ice dams
Ice dams form when attic heat melts snow on the upper roof; meltwater flows down to the cold eaves and refreezes, backing up under shingles. The correct prevention sequence:
- Air-seal the ceiling plane at the attic floor: stop warm interior air from entering the attic. This is the most important step and the one most often missed.
- Insulate the attic floor to keep the roof deck cold (R-50 or more in most Canadian climates).
- Install self-adhered ice-and-water shield at the eaves, extending at least 1 metre past the interior face of the exterior wall (not just to the exterior wall line).
Ventilating the attic (ridge vent plus soffit vents) is a supplementary strategy; it helps keep the deck cold in a properly air-sealed attic, but ventilation alone cannot compensate for warm air bypassing ceiling insulation through penetrations and gaps.
Fenestration
Fenestration (windows, skylights, curtain walls, and glazed doors) is the weakest thermal element of the building envelope. CHING chapter 8 covers doors and windows, including window types and installation; "Windows: Overview of Issues" covers performance metrics and common failure modes.
Performance metrics
- U-value (W/m² K)
- Overall heat transfer coefficient for the complete window unit including the frame. Lower values mean better thermal performance. Double-glazed units: approximately U 1.4 to 2.0. Triple-glazed: approximately U 0.8 to 1.2.
- SHGC
- Solar heat gain coefficient: fraction of incident solar energy entering the building (0 to 1). Higher SHGC = more solar gain. Use high SHGC on south-facing glass for passive heating; use low SHGC on east, west, and where overheating is a risk.
- Visible transmittance (VT)
- Fraction of visible light transmitted (0 to 1). A window can have low SHGC but high VT using selective coatings, admitting daylight while blocking solar heat gain.
- Condensation resistance (CR)
- NFRC rating from 0 to 100; higher values indicate less tendency for condensation on interior surfaces at cold outdoor temperatures.
Glazing and coatings
Insulating glazing units (IGUs) consist of two or more panes separated by a spacer and sealed with inert gas (argon or krypton). Low-emissivity (low-e) coatings reduce long-wave radiation transfer across the cavity. A soft-coat low-e on the second surface (interior face of the outer pane) reduces solar heat gain. A soft-coat low-e on the third surface (interior face of the inner pane of a double unit) reduces heat loss in cold climates. Triple-glazed units add a third pane and second cavity, significantly reducing U-values and condensation risk on the interior surface.
Frame materials
Aluminum frames without thermal breaks have high conductivity and are prone to condensation on interior surfaces in cold climates; a polyamide thermal break reduces this significantly. Vinyl (PVC) frames have low conductivity and require no maintenance. Fibreglass frames have low conductivity, good dimensional stability, and the highest overall thermal performance of common frame materials. Wood frames have good thermal performance but require periodic maintenance. Frame area is typically 20 to 30 percent of the total unit area, so frame U-value substantially affects the whole-unit rating.
Condensation and edge seals
Condensation on the interior surface occurs when the glass temperature falls below the interior dew point. Improving the window U-value raises the interior glass surface temperature; reducing interior relative humidity lowers the dew point. Condensation appearing between panes of an IGU indicates seal failure: the desiccant in the spacer has been exhausted and exterior moisture has entered the cavity.
Mechanical Ventilation
Modern airtight residential construction achieves natural air infiltration well below 0.3 air changes per hour (ACH), the generally accepted minimum for acceptable indoor air quality. Without mechanical ventilation, airtight buildings accumulate CO2, excess humidity, volatile organic compounds (VOCs), and combustion products. The supplementary reference "Why Houses Need Mechanical Ventilation Systems" covers this topic in full.
Why airtight buildings need mechanical ventilation
Older construction relied on gaps and cracks for infiltration to dilute interior pollutants. When those gaps are sealed for energy efficiency, air exchange drops to 0.1 ACH or less. Mechanical ventilation restores fresh air supply in a controlled, predictable way, without depending on wind or stack effect.
Ventilation strategies compared
| Strategy | How it works | Risk in Canadian climates | When appropriate |
| Exhaust-only | Fan exhausts air; makeup air infiltrates through leaks and passive inlets | Negative interior pressure; backdrafting of combustion appliances (furnace, water heater, fireplace) | Older leaky buildings only; not appropriate for new construction |
| Supply-only | Fan pressurizes interior; exhaust through passive vents and exfiltration | Positive pressure drives warm humid air into wall cavities, where it condenses in cold-climate assemblies | Hot-dry climates; rarely appropriate in Canada |
| Balanced (HRV or ERV) | Equal supply and exhaust flow rates; heat or energy exchanged between streams | Requires proper commissioning and regular filter maintenance | All new residential construction in Canada |
HRV vs ERV
A heat-recovery ventilator (HRV) transfers sensible heat between the exhaust and supply air streams using a fixed-plate or rotary heat exchanger. In Canadian winters, the warm exhaust stream pre-heats the cold incoming air, recovering 60 to 80 percent of the heat that would otherwise be lost. The HRV transfers heat only, not moisture: interior humidity is exhausted with the outgoing air.
An energy-recovery ventilator (ERV) transfers both sensible heat and moisture. In very dry climates, retaining some interior humidity in winter improves comfort. In summer, the ERV can pre-condition warm humid outdoor air using the cooler drier interior exhaust stream. ERVs are less common across most of Canada because the priority in winter is removing excess interior moisture, not retaining it.
Local exhaust and demand control
Local exhaust fans in kitchens and bathrooms remove pollutants at the source. A recirculating range hood filters grease and odour but does not exhaust air to the exterior and does not count as ventilation. Demand-controlled ventilation (DCV) uses CO2, humidity, or VOC sensors to reduce ventilation rates in unoccupied or low-occupancy periods, reducing energy use in spaces with variable occupancy.
Key Terms Glossary
- ACH (air changes per hour)
- Volume of air exchanged per hour divided by conditioned volume. 0.3 ACH is the accepted residential minimum for indoor air quality.
- Air barrier
- A continuous assembly or membrane that prevents air leakage through the building envelope. Must be continuous and connected at all joints and penetrations.
- Bearing capacity
- Maximum load per unit area (kPa) that a soil can support without failure or excessive settlement.
- CLT (cross-laminated timber)
- Engineered wood panels with alternating perpendicular laminations. Used as floor, wall, and roof elements in mass timber construction.
- Condensation
- Water depositing on a surface when that surface temperature falls below the dew point of the adjacent air.
- Dew point
- The temperature at which air becomes saturated with moisture and condensation begins; depends on both temperature and relative humidity.
- Diaphragm
- A floor or roof structure that acts as a horizontal plate to collect lateral loads and transfer them to shear walls.
- ERV
- Energy-recovery ventilator; transfers sensible heat and moisture between exhaust and supply air streams. Compare to HRV.
- Frost heave
- Upward displacement of soil or a foundation caused by expansion of water as it freezes. Prevented by bearing footings below the frost depth in well-drained soil.
- HRV
- Heat-recovery ventilator; transfers sensible heat only between exhaust and supply air streams. Standard balanced ventilation choice for most Canadian climates.
- IGU (insulating glazing unit)
- A sealed glazing unit with two or more panes separated by gas-filled cavities. Standard in Canadian construction.
- Linear transmittance (psi, W/m K)
- Heat flow through a linear thermal bridge per unit length per degree of temperature difference. Used in the Building Envelope Thermal Bridging Guide to quantify bridges such as balcony slabs and cladding supports.
- Low-e coating
- A metallic coating on glass that reduces long-wave radiative transfer. Position on the glass surface determines whether it primarily reduces solar gain or heat loss.
- Rainscreen
- A cladding system with a drained and ventilated cavity between the cladding and the drainage plane. Pressure equalization reduces the driving force for water entry.
- SHGC
- Solar heat gain coefficient; fraction of incident solar energy entering the building through a window (0 to 1).
- Shear wall
- A wall sheathed and connected to resist in-plane lateral forces from wind and seismic loads. Must be tied to the foundation to prevent overturning.
- Thermal bridge
- A path of higher thermal conductivity that bypasses insulation, increasing heat flow and reducing the effective R-value of an assembly.
- Tributary area
- The floor or roof area delivering load to a single structural member. Used to calculate total loads on beams, columns, and walls.
- Vapour retarder
- A material that slows moisture diffusion through an assembly. Class I (<0.1 perms): polyethylene; Class II (0.1-1.0 perms): kraft paper; Class III (1.0-10 perms): latex paint. In cold climates, placed on the warm (interior) side of insulation.
Study Approach, Question Patterns, and Common Traps
What to read first
Start with CHING chapters 4 through 8: floor, wall, and roof systems, moisture and thermal protection, and doors and windows are the most heavily tested areas. Then read the Building Envelope Thermal Bridging Guide sections 3 and 4 to add quantitative depth. Finish with "Why Houses Need Mechanical Ventilation Systems" for ventilation questions. CHOP chapters 2.5 and 5.5 add Canadian practice context but are less likely to generate specific calculation questions.
Common question patterns
- Control layer identification: a wall detail is described and you must identify which control layer is missing, misplaced, or discontinuous. Check: is each of the four layers present and continuous?
- Platform frame sequencing: identify the correct order of operations or the component responsible for a given function (e.g., "what member resists racking force on the second-floor wall?").
- Ventilation strategy selection: given a building type and climate, select the correct approach. Balanced HRV is almost always correct for new Canadian residential construction.
- Thermal bridge source: identify which element in an assembly is causing heat loss or condensation that does not match calculated performance. Steel studs, concrete balconies, and cladding supports are the most common answers.
- Ice dam diagnosis: a roof is experiencing ice damming; identify the root cause (typically insufficient attic insulation or air leakage at the ceiling plane) before selecting the fix.
Common traps
- Treating a condensation problem as a ventilation problem: check the control layers first, then consider ventilation changes.
- Confusing waterproofing with dampproofing: dampproofing handles vapour and minor moisture; waterproofing handles hydrostatic pressure. Using dampproofing where waterproofing is required is an error.
- Placing a vapour retarder on the wrong side: in cold Canadian climates, the vapour retarder belongs on the interior (warm side); exterior placement traps moisture in the wall.
- Confusing R-value with effective R-value: an R-20 batt between steel studs may deliver an effective wall R-value of 7 to 9. Continuous exterior insulation is required to approach the nominal value.
- Assuming attic ventilation prevents ice dams without addressing air sealing: ventilation helps but is largely ineffective if warm interior air is bypassing insulation through ceiling penetrations.
Suggested study plan
Allow 14 to 20 hours total. A suggested split: CHING chapters 3-8 (6-8 hours), Building Envelope Thermal Bridging Guide sections 3-4 (2-3 hours), ventilation and windows supplementary references (2-3 hours), Canadian Wood-Frame House Construction selected chapters (2-3 hours), Heating, Cooling, Lighting chapters 2, 3-4, 15 (2-3 hours). Practice questions from Examitect's ExAC study plan will confirm where to focus additional review.